Thershold of hardware monitor
Hello I configured snmp service in XGS2210-24 switches so traps are sent to a snmp monitor. I have a question about this traps
zyHwMonitorFanSpeedOutOfR ange
zyHwMonitorTemperatureOut OfRange
zyHwMonitorPowerSupplyVolt ageOutOfRange
What is the threshold of that alarms that indicate that exist a problem in switch.?
I saw this image
I guess if mac temperature goes above 85, will switch send a trap?
I guess if fan1 speed goes below 500, will switch send a trap?
In voltaje section what mean of +-%6??
Thanks in advance
All Replies
-
Sorry, my switch is XGS3370
0 -
And what is the threshold with this traps
zyHwMonitorPowerSupplyVolt ageOutOfRange
0 -
0
-
Hi @VictorZX
Kindly see my reply in bold.
I guess if mac temperature goes above 85, will switch send a trap? Correct.
I guess if fan1 speed goes below 500, will switch send a trap? Correct.
In voltaje section what mean of +-%6??
It means +-6% of the rated voltage.
For example of rated 5V, 6% threshold of 5V equals 0.3V.
In case the rated 5V is detected lower than 4.7V or higher than 5.3V, the switch will send a trap.
The zyHwMonitorPowerSupplyVoltageOutOfRange monitors rated voltages in the HW monitor table.
By the way, remember to check the trap options in Management -> Access Control -> SNMP -> Trap Group in case you need to monitor them via SNMP trap.
Zyxel_Lucious
0
Categories
- 8.1K All Categories
- 1.6K Nebula
- 59 Nebula Ideas
- 54 Nebula Status and Incidents
- 4.3K Security
- 222 Security Ideas
- 935 Switch
- 41 Switch Ideas
- 818 WirelessLAN
- 19 WLAN Ideas
- 5K Consumer Product
- 136 Service & License
- 266 News and Release
- 52 Security Advisories
- 13 Education Center
- 536 FAQ
- 252 Nebula FAQ
- 132 Security FAQ
- 73 Switch FAQ
- 72 WirelessLAN FAQ
- 7 Consumer Product FAQ
- 34 Documents
- 34 Nebula Monthly Express
- 66 About Community
- 44 Security Highlight